Spent pretty much all day trying to resolve this and am completely out of ideas. I have a Honeywell/Ademco Vista-20P with 4 keypads. For the initial setup of the AD2Pi Network Appliance I selected Address 20. I configured the alarm panel *193 [1] [0] for the AD2Pi.
I can talk to the AD2Pi but it can't talk to the alarm panel. I changed the keypad at Address 18 to 20 and moved the AD2Pi to 18; no change. I've disconnected and reconnected the wiring twice; no change. Applied all updates; no change. Any ideas?
Opening device ✔
Saving device configuration ✔
Keypad communication (Send) ✘ Check wiring and that the correct keypad address is being used.
Keypad communication (Receive) ⚠ Test timed out.
AlarmDecoder device settings:
Address 20
Configbits 0XFF05
Address Mask 0XFFFFFFFFL
Zone Exander Emulation False False False False False
Relay Emulation False False False False
LRR Emulation False
Deduplicate False
Panel Type ADEMCO
Firmware version V2.2a.8.8
Serial Number FFFFFFFF
Device Flags TX;RX;SM;VZ;RF;ZX;RE;AU;3X;CG;DD;MF;L2;KE;M2;CB;DS;ER;CR